By definition the "neutral" in a alternating current system is the grounded conductor. The "ground" is known as the grounding conductor.
Two most common services(United States) are 480v 3phase, mainly commercial, and 220v single phase for residential. A 480v system has 3 277v legs, whereas the 220v system is made of 2 120v legs. Legs are also often reffered to as phases.
In order to use a single 277v or 120v leg of either system, a path to ground is needed. This path to ground creates a difference of potiental, this is the neutral(grounded) conductor. The neutral is derived at the service, at this point the neutral has to be bonded to the grounding system which should include a ground rod and cold water for residental, the system can be required to be a little more complex for commercial 480v systems.
So in residental panels you should see the neutral bonded to the ground, unless the panel is a sub panel. A subpanel would be fed out of the main panel with a seperate neutral conductor and should be kept isolated within the sub panel.
In commercial 480/277v systems transformers are used to create 208/110v power for general use. In this the neutral is derived at the transformer by bonding the neutral to the building steel and the cold water system, which are equipment grounding systems.
If you were to isolate the neutral in your residents and still run power to everything you will be subjecting all your electrical devises to 220v. So you must have the neutral bonded to ground. As a note though in these panels you will see the neutral bar isolated.
Hope this clears up some confusion.
Two most common services(United States) are 480v 3phase, mainly commercial, and 220v single phase for residential. A 480v system has 3 277v legs, whereas the 220v system is made of 2 120v legs. Legs are also often reffered to as phases.
In order to use a single 277v or 120v leg of either system, a path to ground is needed. This path to ground creates a difference of potiental, this is the neutral(grounded) conductor. The neutral is derived at the service, at this point the neutral has to be bonded to the grounding system which should include a ground rod and cold water for residental, the system can be required to be a little more complex for commercial 480v systems.
So in residental panels you should see the neutral bonded to the ground, unless the panel is a sub panel. A subpanel would be fed out of the main panel with a seperate neutral conductor and should be kept isolated within the sub panel.
In commercial 480/277v systems transformers are used to create 208/110v power for general use. In this the neutral is derived at the transformer by bonding the neutral to the building steel and the cold water system, which are equipment grounding systems.
If you were to isolate the neutral in your residents and still run power to everything you will be subjecting all your electrical devises to 220v. So you must have the neutral bonded to ground. As a note though in these panels you will see the neutral bar isolated.
Hope this clears up some confusion.